nsdp + 449 eh April 20, 2021 (edited) 7 hours ago, Ward Smith said: The fundamental problem is all these whiz bang wonderful devices that keep track of and notify us of things run on electricity. Take that away and they're so many paperweights. I recently had a power outage and the utility's website said they were aware of the problem and anticipated repairs to finish in 8 hours. I hooked up my generator, with the same setup that @Jan van Eck described and put my cell number in the notification queue, since I'm now disconnected from the mains. Hours go by and I keep checking the site, which keeps saying 8 hours to go even though 3 have gone by. Long story short, my neighbors asked me why I was running the generator when the power was back up. Turns out the utility's system wasn't getting or giving updates, because no power. I've now given them advice on how to resolve these issues in future. But we live in modern times and count on modern conveniences. The poor IT guy at the utility putting together the notification system bought off the shelf equipment that all runs on electricity. Until you stress test the system, you don't know where the weak links in the chain are. Once power was restored the routers needed rebooting etc. It all looks good on paper I'm sure. It's going to take serious effort in Texas to find those weak links in the chain. It's a big state, lots of moving parts. I also wonder, given the litigious nature of things, whether everyone is interested in saying everything they know, facing Monday morning quarterbacks looking over their shoulders using months to analyze decisions made in seconds in the heat of battle. Telemetering for transmission is done with the PT's and CT's (do you know what those are?) powering WR-8 meters which get their power from the PT's on either a 130,000volt:120 volt ratio or 345,000 volt:120 volt ratios. If there is power in the transmission line then there is power in the meter and the meter is connected by fiber optic cable to the dispatch center. there is NO internet connection on trasnmission adn generation until it enters the disatching center. Also ERCOT is required by CONGRESS signed by Pres. G.W. Bush under the Energy Policy act of 2005 for HVDC ties at OklaUnion( exporting 124mw to SPP in your screenshot.), Montecello(SPP), Del Rio(CFE), Laredo(CFE) and the Valley(CFE) be monitored by OATI.. The export license to connect to CFE requires membership in OATI so you don't know what you are talking about. SPP also requires OATI participation to interconnect to their grid. Your comments on the internet DO NOT APPLY to transmission and generation systems data and relaying since that is 100% fiber optic and not internet for safety reasons. Yourr local distribution can be on the internet if the utility choses. Austion and San Antonio are 100% fiber optic fed from transmsion PT sources. If transmission data and relaying don't have power and data, then the whole grid is blacked out and that did not happen. Unless operators lied to the Railroad Commission 37% of the Freeze offs in the Permian Basin occurred in counties not served by ERCOT. They are served by either Southwestern Public Service or Golden Spread Electric cooperative's distribution coop customers. You better look at GSEC's ownership and see what countties those coops serve. Those would be 100% prodcuer negligence. Edited April 20, 2021 by nsdp 1 Quote Share this post Link to post Share on other sites
Ward Smith + 6,615 April 21, 2021 2 hours ago, nsdp said: Because you took you screenshot 12:49 AM on April 20th dummy. The problem was at 0100 hrs on Feb. 15th some 64 days BEFORE your screenshot. You are two months late to the party. Right needledick, now look back fifty plus pages to the posts at the time with the pretty graphs. You're two months late to this party dickfor, you've missed all the run-up. It's well documented that wind dropped 10gw in a matter of minutes. Even the graph above hints at it, but there are better graphs out there. I'll answer your other insipid comments in a different part 2 1 Quote Share this post Link to post Share on other sites
Ward Smith + 6,615 April 21, 2021 1 hour ago, nsdp said: Telemetering for transmission is done with the PT's and CT's (do you know what those are?) powering WR-8 meters which get their power from the PT's on either a 130,000volt:120 volt ratio or 345,000 volt:120 volt ratios. If there is power in the transmission line then there is power in the meter and the meter is connected by fiber optic cable to the dispatch center. there is NO internet connection on trasnmission adn generation until it enters the disatching center. Also ERCOT is required by CONGRESS signed by Pres. G.W. Bush under the Energy Policy act of 2005 for HVDC ties at OklaUnion( exporting 124mw to SPP in your screenshot.), Montecello(SPP), Del Rio(CFE), Laredo(CFE) and the Valley(CFE) be monitored by OATI.. The export license to connect to CFE requires membership in OATI so you don't know what you are talking about. SPP also requires OATI participation to interconnect to their grid. Your comments on the internet DO NOT APPLY to transmission and generation systems data and relaying since that is 100% fiber optic and not internet for safety reasons. Yourr local distribution can be on the internet if the utility choses. Austion and San Antonio are 100% fiber optic fed from transmsion PT sources. If transmission data and relaying don't have power and data, then the whole grid is blacked out and that did not happen. Unless operators lied to the Railroad Commission 37% of the Freeze offs in the Permian Basin occurred in counties not served by ERCOT. They are served by either Southwestern Public Service or Golden Spread Electric cooperative's distribution coop customers. You better look at GSEC's ownership and see what countties those coops serve. Those would be 100% prodcuer negligence. So, again in a discussion about lost power you pretend it arrived on fairy wings via fiber optic? Data and only data travels on fiber. The internet has nothing to do with it. I've documented the interties >50 pages ago, this isn't FERC quality interconnects, these are miniscule in comparison to the source and sink that is Texas. The knock against Texas, also thoroughly documented prior is that it is an island, not connected like every other state. A tsunami happened and you're talking about buckets of water here and there. But since you're a known blowhard who runs away after humiliation, I'll let you in on a little secret about fiber optic. It needs power due to effects called absorption, dispersion and scattering losses, signals need to be regenerated, typically every 10-15 kilometers depending on frequency and other factors. So yes, fiber can't carry power but it needs power (because of the lasers doncha know). Bet ya didn't know that either dummy. 1 1 Quote Share this post Link to post Share on other sites
Ward Smith + 6,615 April 21, 2021 (edited) Asked and answered, but a refresher course is needed for the slower witted amongst us Graphs that shed light on the ERCOT power crisis Note the date of the article was Feb 17, in the heat of battle as it were. Better numbers have come out since indicating wind was down 10gw not 8. Those are gigawatts @nsdp not megawatts. Edited April 21, 2021 by Ward Smith 1 1 Quote Share this post Link to post Share on other sites
turbguy + 1,543 April 21, 2021 (edited) 5 hours ago, Ward Smith said: So, again in a discussion about lost power you pretend it arrived on fairy wings via fiber optic? Data and only data travels on fiber. The internet has nothing to do with it. I've documented the interties >50 pages ago, this isn't FERC quality interconnects, these are miniscule in comparison to the source and sink that is Texas. The knock against Texas, also thoroughly documented prior is that it is an island, not connected like every other state. A tsunami happened and you're talking about buckets of water here and there. But since you're a known blowhard who runs away after humiliation, I'll let you in on a little secret about fiber optic. It needs power due to effects called absorption, dispersion and scattering losses, signals need to be regenerated, typically every 10-15 kilometers depending on frequency and other factors. So yes, fiber can't carry power but it needs power (because of the lasers doncha know). Bet ya didn't know that either dummy. Yeah, fiber optics have to be "regenerated" after some distance. I believe they do it all optically now, no? I can only assume the power for regeneration is backed up with good UPS's. I doubt it needs much power for that. Probably around, 10-50 watts or so at each site? Edited April 21, 2021 by turbguy 1 Quote Share this post Link to post Share on other sites
Old-Ruffneck + 1,245 er April 22, 2021 18 hours ago, turbguy said: Yeah, fiber optics have to be "regenerated" after some distance. I believe they do it all optically now, no? I can only assume the power for regeneration is backed up with good UPS's. I doubt it needs much power for that. Probably around, 10-50 watts or so at each site? Here is a good site if you want to enlighten the brain some. Single Mode vs. Multimode Fiber Optic Cables | Cleerline SSF Fiber (cleerlinefiber.com) 1 Quote Share this post Link to post Share on other sites
nsdp + 449 eh April 22, 2021 (edited) On 2/15/2021 at 2:40 PM, Eyes Wide Open said: Now just of a second here...i do believe underground pipelines are buried at a depth far below the frost line, actually it would take weeks of subzero temps to freeze any liquid buried 14" below the surface. OK i will ask what am i missing here? Since Ward suggested I look back about 50 pages , I have and found major blunders no one here knows enough to recognize the blunder. Here the problem is methyl hydrate. I am there fore going to explain in English instead of using Reynolds number or Shacham equations or Panhandle A. Paper from Lawrence Berkeley National Lab http://www-eng.lbl.gov/~shuman/NEXT/MATERIALS&COMPONENTS/Pressure_vessels/FM/compressible_pipe_flow.pdf See Example 1. Preventing formation of hydrate plugs Example 1: hydrate formation in a pipeline https://petrowiki.spe.org/Preventing_formation_of_hydrate_plugs Any one with certification in pipeline safety knows this one. At operating pressures in the pipeline above 600 PSIG methyl hydrate will form at ISO. This was the most common freeze off in the fields since well pressures are 2000-6000psig and pipelines usually above 700-800psig. Another freeze off is going through the well head. PV drop is too great because field hands did not reset valves correctly for the temperature of the steel wellhead or did not insulate the Christmas tree. . You have to maintain higher well head pressure to prevent gas expansion lowering the temperature (PV=nrT)where you freeze the brine in the oil/gas mixture. see time mark 8:15 to 8:45 for video of the brine and hydrate from pipelines in this storm. https://www.youtube.com/watch?v=08mwXICY4JM Practical engineering. I will itemize Ward's blunders, but they are so many it maybe a couple of days to itemize them. Ward. Your failure to understand grid protection/relaying techniques needs no further discussion . Neither does his inability to read need any further comment. . Edited April 22, 2021 by nsdp typing errors 1 1 Quote Share this post Link to post Share on other sites
Eyes Wide Open + 3,555 April 22, 2021 39 minutes ago, nsdp said: Since Ward suggested I look back about 50 pages , I have and found major blunders no one here knows enough to recognize the blunder. Here the problem is methyl hydrate. I am there fore going to explain in English instead of using Reynolds number or Shacham equations or Panhandle A. Paper from Lawrence Berkeley National Lab http://www-eng.lbl.gov/~shuman/NEXT/MATERIALS&COMPONENTS/Pressure_vessels/FM/compressible_pipe_flow.pdf See Example 1. Preventing formation of hydrate plugs Example 1: hydrate formation in a pipeline https://petrowiki.spe.org/Preventing_formation_of_hydrate_plugs Any one with certification in pipeline safety knows this one. At operating pressures in the pipeline above 600 PSIG methyl hydrate will form at ISO. This was the most common freeze off in the fields since well pressures are 2000-6000psig and pipelines usually above 700-800psig. Another freeze off is going through the well head. PV drop is too great because field hands did not reset valves correctly for the temperature of the steel wellhead or did not insulate the Christmas tree. . You have to maintain higher well head pressure to prevent gas expansion lowering the temperature (PV=nrT)where you freeze the brine in the oil/gas mixture. see time mark 8:15 to 8:45 for video of the brine and hydrate from pipelines in this storm. https://www.youtube.com/watch?v=08mwXICY4JM Practical engineering. I will itemize Ward's blunders, but they are so many it maybe a couple of days to itemize them. Ward. Your failure to understand grid protection/relaying techniques needs no further discussion . Neither does his inability to read need any further comment. . Perhaps you might address Mr Wards error's, rather than my thoughts and or questions. That would be a rather basic foundation to build upon...just a thought carry on. Quote Share this post Link to post Share on other sites
turbguy + 1,543 April 22, 2021 (edited) 2 hours ago, nsdp said: Ward. Your failure to understand grid protection/relaying techniques needs no further discussion . Yeah, when I first started working on the generation side, I was initially surprised at the number of protective relays on generation. It took a couple years to understand them all (via osmosis, and a little C.P. Steinmetz). Grid/distribution relaying was never my forte, but a lot of it is really serves quite similar purposes. Way to many diff eq's ("difficult equations") for transient analysis. If grid frequency drops, either you increase generation, shed load, or both. There are zero other options. If your dispatchable stuff ain't there, off goes someone's lights. Edited April 22, 2021 by turbguy Quote Share this post Link to post Share on other sites
wrs + 893 WS April 22, 2021 On 4/18/2021 at 10:32 AM, turbguy said: Does your generator installation include an auto-transfer switch? I'm on "ranch power", which tends to be less reliable as there are no backfeeds to employ in the distribution system. I'm at the end of a loooong distribution branch/circuit. If one stepdown transformer on my circuit branch has a "bad day", it trips the entire branch. At least we can see the smoke in the distance. When we call the REA operator to report an outage, she answers "We'll get right on it, as soon I find out who has the truck today". PLANNED distribution outages (where the REA notifies you that power will be intentionally off for system maintenance) occur about once or twice a year. 13 KW Generac here (nat gas fired), at this altitude, it's derated to 9.5 KW (on a warm day). I believe that is built into the Smart Module that comes with the generator. 1 Quote Share this post Link to post Share on other sites
wrs + 893 WS April 22, 2021 So the February royalty checks are both in and we get paid for liquids and residual gas. The independent got $8/mcf for residual and XTO got $19.91/mcf for residual. We made way more on gas than oil in February for all our wells. I guess that the independent didn't get to sell as much at the high rate over the freeze as XTO did and thus had a lower average price for the month. 1 Quote Share this post Link to post Share on other sites
turbguy + 1,543 April 22, 2021 (edited) 1 hour ago, wrs said: I believe that is built into the Smart Module that comes with the generator. An auto-transfer switch normally is installed as part of the home's electrical system, used to protect against backfeeds into the grid. It disconnects home circuits from the grid supply and switches those circuits to the generator, isolating those to "generator only". These are multi-pole double throw purely mechanical contactors with an electromagnetic operator, typically within it's own metal enclosure. Mine operates with a quite audible mechanical "clunk" when switching. If you have something (smart module) connected to the generator only, it won't isolate circuits from the grid. I would be surprised if it were solid state, too. Edited April 22, 2021 by turbguy Quote Share this post Link to post Share on other sites
Ward Smith + 6,615 April 22, 2021 On 4/20/2021 at 10:50 PM, turbguy said: Yeah, fiber optics have to be "regenerated" after some distance. I believe they do it all optically now, no? I can only assume the power for regeneration is backed up with good UPS's. I doubt it needs much power for that. Probably around, 10-50 watts or so at each site? No No Yes Quote Share this post Link to post Share on other sites
turbguy + 1,543 April 22, 2021 7 minutes ago, Ward Smith said: No No Yes Thanx, not my forte'. I had heard they were going optical-only (no intermediary electronics) about a decade ago, since it required less power and could handle multiple signal wavelength. Guess that's still lab-only. I am surprised they don't use UPS's. "The Grid Never Goes Down" is a falsehood. Quote Share this post Link to post Share on other sites
Ward Smith + 6,615 April 22, 2021 14 hours ago, nsdp said: Since Ward suggested I look back about 50 pages , I have and found major blunders no one here knows enough to recognize the blunder. Here the problem is methyl hydrate. I am there fore going to explain in English instead of using Reynolds number or Shacham equations or Panhandle A. Paper from Lawrence Berkeley National Lab http://www-eng.lbl.gov/~shuman/NEXT/MATERIALS&COMPONENTS/Pressure_vessels/FM/compressible_pipe_flow.pdf See Example 1. Preventing formation of hydrate plugs Example 1: hydrate formation in a pipeline https://petrowiki.spe.org/Preventing_formation_of_hydrate_plugs Any one with certification in pipeline safety knows this one. At operating pressures in the pipeline above 600 PSIG methyl hydrate will form at ISO. This was the most common freeze off in the fields since well pressures are 2000-6000psig and pipelines usually above 700-800psig. Another freeze off is going through the well head. PV drop is too great because field hands did not reset valves correctly for the temperature of the steel wellhead or did not insulate the Christmas tree. . You have to maintain higher well head pressure to prevent gas expansion lowering the temperature (PV=nrT)where you freeze the brine in the oil/gas mixture. see time mark 8:15 to 8:45 for video of the brine and hydrate from pipelines in this storm. https://www.youtube.com/watch?v=08mwXICY4JM Practical engineering. I will itemize Ward's blunders, but they are so many it maybe a couple of days to itemize them. Ward. Your failure to understand grid protection/relaying techniques needs no further discussion . Neither does his inability to read need any further comment. . Doofus, go back to when I described clathrates and get back to me. Hint, a clathrate is the same thing as a hydrate, just the more proper scientific terminology. You like to pretend you've got the terminology down, seconds after reading a paper that uses it. I'm doing this on a mobile device with a small screen, I don't blog on my computer so I don't waste more time than I already do here. Therefore I'm disinclined to write long treatises on these subjects. I'm also disinclined to correct every mistake I see, but yours are egregious enough to warrant correction, because you pretend knowledge you don't have. I do believe you're a lawyer, with all the (dis)honor such a profession deserves. You and @Jay McKinsey should get a room. 1 1 Quote Share this post Link to post Share on other sites
Ward Smith + 6,615 April 22, 2021 3 minutes ago, turbguy said: Thanx, not my forte'. I had heard they were going optical-only (no intermediary electronics) about a decade ago, since it required less power and could handle multiple signal wavelength. Guess that's still lab-only. I am surprised they don't use UPS's. "The Grid Never Goes Down" is a falsehood. Optical "regeneration" involves doping the fiber then firing a laser at that doping (simplified explanation here, I know far more than I can or should describe, still being under multiple non disclosure agreements). One could "say" it's optical only but that laser gets powered how? I also worked on submarine systems, which bend every law of physics they can find to "manage" to get that signal across the ocean. The "grid" goes down all the time, the internet manages to stay up primarily because of BGP routing protocol. Sadly, while vendors will tell you they've run redundant fibers, they've run them in the same conduit. Once a fiber seeking backhoe finds one, it's found them all. Utilities run fiber inside their power lines, but it's the cheap stuff using LED lasers that need regen quite often, sometimes every mile. Low bandwidth compared to other fiber systems but high dispersion losses. Quote Share this post Link to post Share on other sites
turbguy + 1,543 April 22, 2021 (edited) 2 hours ago, Ward Smith said: Optical "regeneration" involves doping the fiber then firing a laser at that doping (simplified explanation here, I know far more than I can or should describe, still being under multiple non disclosure agreements). One could "say" it's optical only but that laser gets powered how? I agree that optical regen could still require distributed power down the fiberline (stil gotta power lasers at regen sites). You gotta amplify and sharpen the signal pusles/phase back up and restore timing (damn you, jitter) after degradation. I thought interferometers, wave plates (and such) were involved in the 'magic. Things evolve. Yup, not my forte'. It gets powered from whatever is around, AC or DC. If there's no power, they lose. Edited April 22, 2021 by turbguy 1 Quote Share this post Link to post Share on other sites
addsco22 0 JH April 22, 2021 To bad Texans are not smart enough to heat trace their wind mills. I guess Texans think there are no wind mills north of Arkansas. Maybe they should learn to maintain their facilities. It would be a lot cheaper than trying to scam their rate payers out of billions for 2 days of power. Time to lock the crooks up for business fraud. Quote Share this post Link to post Share on other sites
nsdp + 449 eh April 22, 2021 (edited) 4 hours ago, turbguy said: I agree that optical regen could still require distributed power down the fiberline (stil gotta power lasers at regen sites). You gotta amplify and sharpen the signal pusles/phase back up and restore timing (damn you, jitter) after degradation. I thought interferometers, wave plates (and such) were involved in the 'magic. Things evolve. Yup, not my forte'. It gets powered from whatever is around, AC or DC. If there's no power, they lose. Ward , you are forgetting that all critical paths in ERCOT are dual path and most all are parallel path. That means you have power from both ends of the transmission lines that connect the substation. If one side goes down you still have at least a radial feed from the other side. So unless a substation is an isolated tap (not loop tap, or loop or ring buss or a breaker and a half or double breaker scheme) you will still have power in the substation from the metering PT's from at least one circuit feeding the station to energize all of your fiber optic cable. So every time you connect two substations you have power at both substations to energize your regen equipment. If you have both lines down , then the substation has no power to worry about monitoring. As for both cables being in the same conduit, where did you see that or is that BS again. You may see it for local distribution The NERC standards require the fiber optic for any transmission line(does not apply to the distribution circuit that goes from the substation to your house), outside the control room, be at least 25 ft from any other fiber optic cable and buried 6 ft below the surface. If the surface is concrete or other impervious material then it has to be in a 2" conduit with a green telecommunications tape overlaying the conduit as a warning for any one digging. You have to mark and put up signs jut like you do for underground electric lines or pipelines of any kind. There are older installations or backup fiber that is installed overhead on the same poles as the power lines. Sounds like you don't know the difference between transmission/generation controls and relaying and distribution controls and relaying. Edited April 22, 2021 by nsdp 1 Quote Share this post Link to post Share on other sites
Ward Smith + 6,615 April 23, 2021 4 hours ago, nsdp said: Ward , you are forgetting that all critical paths in ERCOT are dual path and most all are parallel path. That means you have power from both ends of the transmission lines that connect the substation. If one side goes down you still have at least a radial feed from the other side. So unless a substation is an isolated tap (not loop tap, or loop or ring buss or a breaker and a half or double breaker scheme) you will still have power in the substation from the metering PT's from at least one circuit feeding the station to energize all of your fiber optic cable. So every time you connect two substations you have power at both substations to energize your regen equipment. If you have both lines down , then the substation has no power to worry about monitoring. As for both cables being in the same conduit, where did you see that or is that BS again. You may see it for local distribution The NERC standards require the fiber optic for any transmission line(does not apply to the distribution circuit that goes from the substation to your house), outside the control room, be at least 25 ft from any other fiber optic cable and buried 6 ft below the surface. If the surface is concrete or other impervious material then it has to be in a 2" conduit with a green telecommunications tape overlaying the conduit as a warning for any one digging. You have to mark and put up signs jut like you do for underground electric lines or pipelines of any kind. There are older installations or backup fiber that is installed overhead on the same poles as the power lines. Sounds like you don't know the difference between transmission/generation controls and relaying and distribution controls and relaying. Right and SONET was bullet proof because there were dual rings. What happened to SONET again? Let's see, just the big 3 vendors 20 years ago had annual sales over $200 billion. Today all SONET sales combined don't add up to $40 million. It just didn't work, kind of like your post. SCADA systems require loads of inputs and certainly the ability is there, except when it isn't. Pop quiz, what percentage of grid infrastructure is overhead versus underground? No utility is digging 6 foot deep holes to monitor overhead lines. I know how this is done, you've read about it. The CEO of the number one vendor in that industry is s friend of mine as are several of his employees. You're talking out your… hat let's say. 1 1 1 Quote Share this post Link to post Share on other sites
nsdp + 449 eh April 23, 2021 (edited) 22 hours ago, Ward Smith said: Right and SONET was bullet proof because there were dual rings. What happened to SONET again? Let's see, just the big 3 vendors 20 years ago had annual sales over $200 billion. Today all SONET sales combined don't add up to $40 million. It just didn't work, kind of like your post. SCADA systems require loads of inputs and certainly the ability is there, except when it isn't. Pop quiz, what percentage of grid infrastructure is overhead versus underground? No utility is digging 6 foot deep holes to monitor overhead lines. I know how this is done, you've read about it. The CEO of the number one vendor in that industry is s friend of mine as are several of his employees. You're talking out your… hat let's say. Ward. I suggest you read the NERC standards, no SCADA for RTO or ISO use. A utility may use it for local matters like distribution. . Old generation and transmission installations have to be replaced. There are two reasons why fiber optic cable at least 6 ft. underground. If you drive along Tradewinds Road starting it Harrington Power Plant in Amarillo and go south along the 135 miles of fiber cable adjacent to the 230kv line that connects to Abernathy you will find steel posts with orange signs that say buried fiber optic cable every time they cross a road. The fiber optic is buried for two reasons. 1. there are nuts on the wheel like Ward Smith driving on public roads and 2. to protect against EMP Pulse. Protecting U.S. Electric Grid Communications from Electromagnetic Pulse https://www.resilientsocieties.org/uploads/5/4/0/0/54008795/protecting_us_electric_grid_communications_from_emp.pdf and here is NASA's standard which has been adopted by NERC in 2013 https://www.federalregister.gov/documents/2020/05/04/2020-09695/securing-the-united-states-bulk-power-system Guide to Mitigating Spacecraft Charging Effects ( I can get a signed copy for you from Hank he was my senior roommate in college) as an authoritative standard for preventing celestial disruption as experienced by Hydro Quebec in 1989 or if some one should do something like Star Fish Prime. Guide to Mitigating Spacecraft Charging Effects (nuclear weapons exploded at altitude as happened in Hawaii 's telecommunications and parts of the grid on Kauai and Oahu). If you aren't already familiar with these two events with out looking them up and also know what is called a Carrington Event you have absolutely no business posting anything about grid or powerplant control systems, installation, and protection. FERC White Paper announcing why we do this instead of using stupid ideas like your internet. https://www.ferc.gov/sites/default/files/2020-05/ferc_executive_summary.pdf I guarantee you don't know how it is done and meet the current NERC standards. What happened to SONET is FERC has killed it because it failed in the 2003 Blackout blackout triggering extraneous outages in Maryland and Virginia and failed subsequent NIST testing for grid use. Phones can go out of service and no one dies. Grids go out and people die. 111 died in Texas ice storm. The grid does not quite use the "Manned Rated" standard that NASA uses but we are getting close. Edited April 24, 2021 by nsdp Quote Share this post Link to post Share on other sites
Old-Ruffneck + 1,245 er April 25, 2021 Done?? Finally lol 1 1 Quote Share this post Link to post Share on other sites
Ward Smith + 6,615 April 26, 2021 On 4/23/2021 at 4:34 PM, nsdp said: The fiber optic is buried for two reasons. 1. there are nuts on the wheel like Ward Smith driving on public roads and 2. to protect against EMP Pulse. Why anyone driving on public roads is a problem is unexplained by you but let's all laugh at your second point. An EMP pulse does nothing to the fiber. At. All. Electromagnetic signals of all kinds can be immediately adjacent to fiber, this is why they put it right inside the high voltage wires. Now, do I believe bunglecrats like your butt buddy roommate don't understand simple physics but create onerous regulations based on their ignorance? Why yes, yes I do. 2 Quote Share this post Link to post Share on other sites
Anu Patel 0 April 26, 2021 Who want to miss the chance of double up the salary by stocks, with Secure Investing on Correct way, right no one Hurry up!! Visit Swastika Investmart Ltd we offer quality of way to invest on money & Huge Profit. Soon filled Detail so covid ways doesn’t affect your financial condition. Visit - https://www.swastika.co.in/ Quote Share this post Link to post Share on other sites
turbguy + 1,543 April 27, 2021 (edited) This might be "done", but the complaints over high pricing during an emergency continues. Somebody's gonna pay. The Texas Governor seems to be a target. https://www.houstonchronicle.com/politics/texas/article/All-night-ERCOT-meeting-raises-questions-about-16124189.php The Rural Electrification Agency was created to provide electric power to rural America, including much of Texas. Rural electric coops were responsive to their consumer-owners. Now, Texas electricity providers are investor owned. This is where Texas is with electric power. Sadly, the next great catastrophe waiting to happen might be in food. Farms are no longer family-owned, they are corporate owned. We can expect food prices to rise as a call for returns on investment. Be careful what you ask for when you call for an end to Big Government and deregulation. We've just had a taste of how Big Corporations might treat us. Edited April 27, 2021 by turbguy Quote Share this post Link to post Share on other sites